These are not same design as what switch/receptacles have for the clamping function either though so you can't really make such comparisons.I'm sure some older electricians in here remember when devices used to be able to be backwired (stab-in) with #12 conductors. In the late 80's or early 90's I believe they started making them so we could only backwire with a #14 conductor. The reason for this change was because the thin piece of metal that held the conductor in place tended to fail when it saw the heat from over 15 amps of current. I never use the backwire function even with #14 wire. I prefer to side-wire around the screws. That's why I don't trust Wago connectors in higher current situations.
Also the way they are used vs a back-stab makes a huge difference. For example, on a receptacle with a back-stabbed conductor, everytime you plug/unplug something you are moving the receptacle slightly. That constant moving can loosen, or weaken, the connection. With a Wago type connector, the conductors are just inserted in the Wago itself. So pushing/moving the receptacle has no such effect on the connection in the Wago.These are not same design as what switch/receptacles have for the clamping function either though so you can't really make such comparisons.
I think they are a great product, but I dislike the fact that there are mixed messages in their voltage ratings. UL indicates 600V if you read the datasheet, but the product is stamped with 300V, due to the rating according to other testing standards. This will mean an inspector could possibly make you jump through a lot more hoops to justify their use, if you intend to use them in a 600V application.What's your thoughts on the Wago 221 wire connectors? I think they are much easier to use and a lot quicker to make splices. I know there a little pricy. Anyone using these connectors?
A receptacle also can put additional strain on the connection point when pushing the device into the box, probably does help to "train" the conductors before pushing in though, where with the Wago connector you typically will be pushing more on the conductors and not so much the connector itself when tucking them into the box.Also the way they are used vs a back-stab makes a huge difference. For example, on a receptacle with a back-stabbed conductor, everytime you plug/unplug something you are moving the receptacle slightly. That constant moving can loosen, or weaken, the connection. With a Wago type connector, the conductors are just inserted in the Wago itself. So pushing/moving the receptacle has no such effect on the connection in the Wago.
