Vincent Hetrick
- Florida
- EC
does the 2017 code require 2 ground rods for a subpanel when it is located outside (not in a building). also what is the code article pertaining to this?
The requirement for ground rods at a separate building was in the NEC when I started in the trade in 1978, and likely many years before that.does the 2017 code require 2 ground rods for a subpanel when it is located outside (not in a building). also what is the code article pertaining to this?
no buildings are involvedThe requirement for ground rods at a separate building was in the NEC when I started in the trade in 1978, and likely many years before that.
there is no building involved, these are all standalone panels in a rv parkThe requirement for ground rods at a separate building was in the NEC when I started in the trade in 1978, and likely many years before that.
the service nor the new sub panel are in nor attached to a building. they are in a rv parkIs the sub panel attached to the same building that feeds the sub panel? If so, then no rods are needed.
no buildings involved. all equipment (service and sub panel) are in a rv parkSee NEC 250.32
That has nothing to do with the panel being detached from the building with the service, if the panel is standing alone it needs the GESthe service nor the new sub panel are in nor attached to a building. they are in a rv park
250.32 says "buildings OR STRUCTURES."no buildings involved. all equipment (service and sub panel) are in a rv park
What if it's mounted to a tree?250.32 says "buildings OR STRUCTURES."
I would think the subpanel is mounted to some type of structure.
it is in an open field and attached to a 4x4250.32 says "buildings OR STRUCTURES."
Yes we got that. Please look up definition of structure.the service nor the new sub panel are in nor attached to a building. they are in a rv park
Sounds like somebody is going to get a good work out.in that since every rv location would require a GEC. each rv site has a panel with single 20 single 30 and 2 pole 50 breakers. that would put 300 ground rods in just so satisfy that.