petersonra
Senior Member
- Location
- Northern illinois
- Occupation
- Semi-retired engineer
So, today I got to the clients location to continue a startup, one of the field electricians told me that he had to shut off power to the control room for a while. I asked him why. He said they had found that the panel that they had wired power out of that was labeled 208 120 was actually fed by a 240 volt high leg delta transformer. One of the phases was like 200 volts to neutral instead of 120. God knows how long it's been that way.