I want to use a set of 4/0 Al ser cables on load side of 400 amp meter breaker to terminate in a can over my two 200 amp load centers in basement fifty feet away then tap off with squid lugs or tregos with 4/0 single conductors for the two panels below it. Distance from can to panels is just a 6”nipple. I think this is ok because I’m maintaining requirements for parallel feeders and tap rule. What do you think? Inspector is almost on board.
 
They are on the inside through a crawl space. I thought the egc in the cables were ok if parallel. No
?
Good point.
that’s the easy part. The whole thing driving this is I couldn’t get a 320 meter base with a 200/200 breaker section. Wound up with the meter/400 combo. Still can’t get the 320 until December
 
The article section would be 250.122(F), take note of the last sentence
 
two 200 amp load centers in basement fifty feet away then tap off with squid lugs or tregos with 4/0 single conductors for the two panels below it.
The Parallel #4/0's are fine if the EGC within each cable is the correct size. The #4/0 tap conductors are too small for a 200 amp OCPD.
 