Peter@SurePower
Member
- Location
- Newport Rhode Island
- Occupation
- Electrical Contractor
I want to use a set of 4/0 Al ser cables on load side of 400 amp meter breaker to terminate in a can over my two 200 amp load centers in basement fifty feet away then tap off with squid lugs or tregos with 4/0 single conductors for the two panels below it. Distance from can to panels is just a 6”nipple. I think this is ok because I’m maintaining requirements for parallel feeders and tap rule. What do you think? Inspector is almost on board.