AFCI Bathroom Upgrade
JHarbinson
SF Bay Area
GC
Remodeling a bathroom. Installed new dedicated 20A circuit but panel (Siemens) only has room of a single narrow breaker so unable to use an AFCI breaker. 12ga NM already run from panel to bathroom (done by others before I arrived). My thought is install a dead front combo AFCI/GFCI in a box just above the panel fed by MC or EMT then feeding the NM. Sound kosher or do I need to rerun the NM as MC to the outlet and use a OBC combo AFCI/GFCI?
Under '17 NEC, the bath circuit is not required to be AFCI.
Same is true for the 2020
210.12 Arc-Fault Circuit-Interrupter Protection.
Arc-fault circuit-interrupter protection shall be provided as required in 210.12(A), (B), (C), and (D). The arc-fault circuit interrupter shall be installed in a readily accessible location.
(A) Dwelling Units.
All 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets or devices installed in dwelling unit kitchens, family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, laundry areas, or similar rooms or areas shall be protected by any of the means described in 210.12(A)(1) through (6):
Thanks for the clarification. I was thrown by 210.12B as indicated in my 8th edition “code check” book stating “Req’d for all 120V 15A & 20A branch circuits supplying outlets and devices in dormitory unit bedrooms, living rooms, hallways, closets, bathrooms & similar rooms”
And not only that but what Siemens panel uses 1/2 size breakers?
I’ve never seen one
Only panel I'm aware of is GE that has narrow breakers. Siemens does now have tandem AFCI breakers but that is not a 1/2 size breaker.
Is OP an electrician? Profile says GC.
Crouse-Hinds, Challenger, & FPE, did also but 3 all are defunct.