The question was posed to me in an I.M. and I didn't think to do the math (I was assuming a 40 amp load). The question centered around any requirement to size the branch circuit at 125% and, although most heating loads are figured at 125%, I could find no justification to do so from the steam generator.I see that as a non-continuous load so per 210.19(A)(1) so you need 6AWG copper NM for that.
Yes. You could use 40 amp circuit conductors and a 40 amp OCPD for a 40 amp non-continuous load.Are you in agreement that if the load was 9.6kw, a #8 would be sufficient ?
I don't see a need for the 125%, and if the load is 9.6kW, then a 40 amp conductor is fine.The question was posed to me in an I.M. and I didn't think to do the math (I was assuming a 40 amp load). The question centered around any requirement to size the branch circuit at 125% and, although most heating loads are figured at 125%, I could find no justification to do so from the steam generator.