4000w of heat on the same circuit

Status
Not open for further replies.

HamElec

New User
Location
Pennsylvania
Occupation
Electrician
So I have a customer that wants electric heat in her movie room that is being built in her basement. I took the dimensions of the room and its 408 Sq Ft at 10 watts per sq ft comes out to 4080w of heat. She would like to use the in wall fan forced heaters. I was going to get two, 2000w heaters and put one on either side of the room. I know this is too much to put on a 20a circuit, so I would like to run 10/2 and put it on a 25a breaker. My main area of concern is the thermostat. I see that both Honeywell and Marley 4 wire stats are only rated for 22amps. These are the two brands carried by my local supply house. Does it pose a risk to put the thermostat on a 25a or 30a breaker? Every house that Ive wired that was to be heated with electric, was tiny and only needed a couple circuits. Ive only done a handful of houses that needed electric heat in my 13 year career, so if there may be a better solution or product I'm all ears and appreciate the help.
 
I would use two 'stats. In cases where only a small amount of heat is needed, one heater can supply the demand. Set the two stats a few degrees apart so that both heaters are energized only when there is adequate demand.
 
I think 4kW seems like an awful lot heat for something like a 20 ft by 20 ft room. How high is the ceiling?
 
I think 4kW seems like an awful lot heat for something like a 20 ft by 20 ft room. How high is the ceiling?
I agree since it is a basement room. But, this is a I want it hot now, not keep it hot for days, so extra KW is good.

A line voltage thermostat is 22 amps. 22 x 120 = 2640 watts. Two of those circuits is 5280 watts. What's the question?

I would go with 240 volt heaters, and baseboard at that. Who wants FAN NOISE in a movie room??????

Two baseboard heaters total of 4 to 5 KW, each on a thermostat, should heat it up nice and quiet too.
 
I like King Pic-A-Watt heaters, can easily adjust heater wattage. Use a quality digital T-stat, the old knob T stats have a wide deadband on temp. Some t stats from King have Bluetooth and cell phone app
 
I agree that the sizing of heating equipment should be based on the heat loss through the envelope, however the 10 W/ft2 rule of thumb seems to be very very common.

On the other hand post #7 makes a very good point. It is very likely that this room will be cold except when in use, and you probably want something oversized that will heat the room quickly.

-Jon
 
It may be common, but it doesn't take the thermal insulative properties of the walls & windows into consideration.
And if it's applied to floor area, it's not just incomplete, it's completely wrong.

Like most “rules of thumb”, the person using it needs to be aware of its limitations, lest they get bitten in the proverbial behind!
 
Where did 10 W/ft2 come from? Somebody's rectal research?
This rule of thumb for baseboard heat works for most every case. Thermostats will make sure the room is not overheated. Sure, a real Manual J or using the loadcalc.net site will get a closer answer*. Then when the power is off for an extended time, the house takes way longer to heat back to temperature. What savings is that? The extra few feet of baseboard heat is minimal in price.

Now, installing HVAC systems, yep, be more on the mark. ;)

* then one has to convert BTUs to watts....
 
So I have a customer that wants electric heat in her movie room that is being built in her basement. I took the dimensions of the room and its 408 Sq Ft at 10 watts per sq ft comes out to 4080w of heat. She would like to use the in wall fan forced heaters. I was going to get two, 2000w heaters and put one on either side of the room. I know this is too much to put on a 20a circuit, so I would like to run 10/2 and put it on a 25a breaker. My main area of concern is the thermostat. I see that both Honeywell and Marley 4 wire stats are only rated for 22amps.
I dont see a issue with the 22 amp stat, not a NEC issue. I believe the stat or relay just needs to be sized for the load. Look a t most dimmers rated 300 Watts.
 