250.118 Types of Equipment Grounding Conductors. The
equipment grounding conductor run with or enclosing the
circuit conductors shall be one or more or a combination of
the following:
(1) A copper, aluminum, or copper-clad aluminum conductor.
This conductor shall be solid or stranded; insulated,
covered, or bare; and in the form of a wire or a busbar of
any shape.
(2) Rigid metal conduit.
(3) Intermediate metal conduit.
(4) Electrical metallic tubing.
(5) Listed flexible metal conduit meeting all the following
conditions:
(6) Listed liquidtight flexible metal conduit meeting all the
following conditions:
(7) Flexible metallic tubing where the tubing is terminated
in listed fittings and meeting the following conditions:
(8) Armor of Type AC cable as provided in 320.108.
(9) The copper sheath of mineral-insulated, metal-sheathed
cable Type MI.
(10) Type MC cable that provides an effective ground-fault
current path in accordance with one or more of the
following:
(11) Cable trays as permitted in 392.10 and 392.60.
(12) Cablebus framework as permitted in 370.60(1).
(13) Other listed electrically continuous metal raceways and
listed auxiliary gutters.
(14) Surface metal raceways listed for grounding.