ggunn
- Austin, TX, USA
- Consulting Electrical Engineer - Photovoltaic Systems
Interesting for you, maybe, but not for me. I just need to come to an agreement with the utility, design the system, and move on to the next project. I don't have the desire to tilt at those particular windmills.It would be interesting to ask one of these POCOs (or do it as a two step process and see what happens) if you could submit A non PV application to"upgrade the service" by adding the additional service conductors and service panel, and once that is completed, submit another separate application for a load side PV connection. Perhaps that would make them realize the absurdity of their position.
At times I have submitted a design that the utility has rejected, and I have responded with code references that showed it to be NEC compliant, to which the utility has responded that they don't care, it is rejected, anyway. That's just the way it is and it's not my lot in life to change it. I have always found another way that the utility would approve, often with their assistance. Life goes on.