S Stevenfyeager Senior Member Location United States, Indiana Occupation electrical contractor Aug 9, 2022 #1 When splicing a circuit in a service panel to run to a subpanel, do we splice the ground too or leave the ground in the bus bar ? thank you
When splicing a circuit in a service panel to run to a subpanel, do we splice the ground too or leave the ground in the bus bar ? thank you
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Aug 9, 2022 #2 Leave it where it is. You're welcome.
S Stevenfyeager Senior Member Location United States, Indiana Occupation electrical contractor Aug 10, 2022 #3 LarryFine said: Leave it where it is. You're welcome. Click to expand... thank you
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Aug 10, 2022 #4 300.3(B) will enter into this. If the feeder conductor to the subpanel is not in the same raceway or cable as the branch circuit conductor, the neutral for the branch circuit must originate in the subpanel.
300.3(B) will enter into this. If the feeder conductor to the subpanel is not in the same raceway or cable as the branch circuit conductor, the neutral for the branch circuit must originate in the subpanel.