splicing circuits in panel, grounds splice too ?

Status
Not open for further replies.

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
300.3(B) will enter into this. If the feeder conductor to the subpanel is not in the same raceway or cable as the branch circuit conductor, the neutral for the branch circuit must originate in the subpanel.
 