dont_blow_up
- USA
- mechanical engineer
Hello all. I really love this forum and have anonymously used it for years, but this is my first post. Go easy on me since I'm just a mechanical engineer who happens to also do electrical stuff sometimes.
Scenario 1 (fixed equipment):
I have a C1D2 classified area, which is an entire room in the building. In the C1D2 area, there is various process control equipment (sensors, solenoids, etc.) that all gets controlled with a PLC. The room is basically a weird LPG engine test chamber. I'd like to get confirmation of my understanding of the NEC as it relates to the low voltage control field wiring.
Options for field wiring:
Scenario 2 (temporary equipment, LPG engine):
The other scenario is the LPG engine that is being tested in the room. It is not rated nor listed in any way, and it never will be since it's all R&D. I need to get something like 100A at 24VDC to this engine to crank it over, and I'm not sure how to do it. So far, I have the DC power supplies located outside of the C1D2 area, and I have massive 24V cables and many smaller data cables running through that fire proof passthrough to the equipment. I would like to have something more permanent, but I don't know how to achieve this since the test equipment is not rated for the area. Any ideas?
- Use ex proof process control equipment -> conduit run out to the non-classified area with conduit seals -> wire into the PLC enclosure in the non-hazardous area (I believe this meets NEC requirements)
- Use ex proof process control equipment -> conduit run to an ex proof junction box inside the classified area -> listed connectors in the classified area -> PLTC-ER cable route from the connector in the hazardous area to the non-hazardous area -> wire into the PLC enclosure in the non-hazardous area (I believe this meets NEC requirements)
- Option 1 for passing through the wall between the C1D2 and non-haz locations: route the PLTC-ER in conduit with a seal through the wall (I believe this meets NEC requirements)
- Option 2 for passing through the wall between the C1D2 and non-haz locations: route the PLTC-ER through a fire rated passthrough through the wall
- The gas cannot be transmitted through the cable and into the PLC enclosure because of the listed connectors, so I believe this meets NEC requirements; however, it also means that there is a way for gas to leave the room, in general. I believe this would (or could) result in a small classified area outside of the room per NFPA 497. The AHJ signed off on this, FWIW, and I would like to get some feedback here.
- Use nonincendive process control equipment in the classified area -> any wiring method to PLC -> wire into the PLC enclosure (I believe this meets NEC requirements)
- This assumes the wiring is done per the control drawings of the PLC hardware and the nonincendive field device, of course
- Similar options for the passthrough in the wall as stated above
- Intrinsically safe stuff (not used, but I understand that this is also an option along with purged enclosures and ex proof boxes)