- Location
- Mission Viejo, CA
- Occupation
- Professional Electrical Engineer
Not every Subsection [501.140(A)(1) through (A)(5)] must necessarily apply; however, I understand your quandary.The way I read 501.140(A), it doesn't comply because the connections to the engine are not listed type connections, of course. On the test chamber side of the connection, I'm not sure what sort off connection to use. I'm having a hard time finding anything that would meet code. I'm also not sure how to meet 501.140(B)(2) as well. The engine has its own separate grounding connection that isn't part of the 24V power supply to it. It's unclear to my reading of it if that's acceptable per NEC. It's also unclear to me how to properly seal these connections or if it's even required. I don't want them potted because the different engines get their electrical harnesses swapped out regularly, so I can't really pot them through conduit and the cables can technically pass gas through the connection at the engine to the non classified space.
It would appear to me that yours is an application of 501.140(A)(5). In this case,“portable,” simply means it can be moved, but not necessarily that it will be moved, after final installation. From the Merriam-Webster 11th Collegiate Dictionary (the NFPA dictionary for Definitions not in the referenced standard):
It appears to me, the real problem such as it is, is Section 501.140(B)(4).adjective
por·ta·ble
| \ ˈpȯr-tə-bəl \
Definition
- 1a: capable of being carried or moved about
Since you convinced your AHJ that this is a Division 2 location, read the last sentence. Where explosionproof equipment is required, I would probably fashion “whips” from the explosion proof equipment to otherwise listed cord connectors and convince the AHJ that this is an application of 590.3(C).
Bonding is another critical issue of Section 501.140(B)(2). That would be an issue in it’s final installation as well assuming that the assembly will ultimately be installed in a classified location. See Section 501.30.