Do two 100A-rated wires = 200A-rating?

Status
Not open for further replies.
Location
Madison, WI
Occupation
Master Electrician (Residential and small-scale commercial)
Could I use a connector to connect (2) #3 CU THHN with (1) 3/0 CU THHN and then connect that 3/0 to a 200A panel? I have multiple 100 amp feeds coming into a J-box from a multi-position meter enclosure where only one meter is used and trying to combine from multiple 100 amp panels to one 200 amp panel.
 
Could I use a connector to connect (2) #3 CU THHN with (1) 3/0 CU THHN and then connect that 3/0 to a 200A panel? I have multiple 100 amp feeds coming into a J-box from a multi-position meter enclosure where only one meter is used and trying to combine from multiple 100 amp panels to one 200 amp panel.

No.

You are asking about 'parallel conductors', which are allowed by the NEC, but only in 1/0 or larger.

-Jon
 
Please forgive me as I'm overstepping my original question. This is an old Murry meter enclosure - I have no other markings I can find on it. Anyone know whether the bottom lug (white wire) would accept a 3/0?
68v1BA7JQH25Ju_0-km7XFPHVEfZzYQ31GHIJ5-KYG2puF40RYOiWkFJ8pbOqDdeLjf6FSuTQVY2BgLXiq2KvSOCkcRqeBnDlRb-rMErFRoR2gf6uyLTk1xCIogZMaJrG9u0m95GDcEPaHLAydRg80mmE-vztskxJDqy-oxUJCBfAfmRtuJi5j5cvA
 
Could I use a connector to connect (2) #3 CU THHN with (1) 3/0 CU THHN and then connect that 3/0 to a 200A panel? I have multiple 100 amp feeds coming into a J-box from a multi-position meter enclosure where only one meter is used and trying to combine from multiple 100 amp panels to one 200 amp panel.
You can't do that but you could take two 1/0 aluminum wires in parallel instead of the number three copper and connect them to the 3/0 copper.
 