That label doesn't say a fuse is required.
It indicates Maximum Fuse size of 35 amps.
If the max fuse size is not needed, why would one be held to installing a fuse at all?
JAP>
I was always taught that “Max fuse size” means a fuse is required.
If it said “Maximum OCPD”, would you think that no OCPD is required if you didn’t need the max?
That's what I had been taught too but where in the NEC does it say that?I was always taught that “Max fuse size” means a fuse is required.
It gets down to 110.3(B) and the product standard for the equipment. The product standard requires that the type and maximum size of OCPD be on the nameplate. Where the type of OCPD shown on the nameplate is a fuse, you are only permitted to use a fuse.That's what I had been taught too but where in the NEC does it say that?
I have not seen one with that marking in a long time. Typically that marking predates the HCAR breakers which have been around for at least 3 decades now. It has to do with the protection of equipment that has multiple motors, and standard breakers did not do a good job with that.
When the HCAR breakers first came out, the name plate marking would often say "fuse of HCAR breaker". Now most just say OCPD because all listed breakers are HCAR breakers.
So this is a UL standard and has nothing to do with the NEC?It gets down to 110.3(B) and the product standard for the equipment. The product standard requires that the type and maximum size of OCPD be on the nameplate. Where the type of OCPD shown on the nameplate is a fuse, you are only permitted to use a fuse.
Respectfully: With 110.3(b) involved, I don't think we can say it has "nothing to do with the NEC".So this is a UL standard and has nothing to do with the NEC?
Thank you for this information. I learned something!Serial Number: 33AM2821 = Assemble in Mexico, Week 28, Year 2021
What I meant was there is no NEC section that uses the wording fuses only in the NEC.With 110.3(b) involved, I don't think we can say it has "nothing to do with the NEC".
No, that is only covered in the listing and labeling requirements.What I meant was there is no NEC section that uses the wording fuses only in the NEC.