Have to use fused disconnect if the walk-in freezer compressor name plate state "Max. Fuse Size"?

Status
Not open for further replies.

jap

Senior Member
Occupation
Electrician
That label doesn't say a fuse is required.

It indicates Maximum Fuse size of 35 amps.

If the max fuse size is not needed, why would one be held to installing a fuse at all?

JAP>
 

retirede

Senior Member
Location
Illinois
That label doesn't say a fuse is required.

It indicates Maximum Fuse size of 35 amps.

If the max fuse size is not needed, why would one be held to installing a fuse at all?

JAP>

I was always taught that “Max fuse size” means a fuse is required.

If it said “Maximum OCPD”, would you think that no OCPD is required if you didn’t need the max?
 

jap

Senior Member
Occupation
Electrician
I was always taught that “Max fuse size” means a fuse is required.

If it said “Maximum OCPD”, would you think that no OCPD is required if you didn’t need the max?

The breaker feeding the disconnect takes care of the OCP part of it.

If you have a 30 amp breaker feeding the disconnect for the OP"s unit you wouldn't have met the max fuse size of 35 amps.

So why would a fuse be needed?

JAP>
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
That's what I had been taught too but where in the NEC does it say that?
It gets down to 110.3(B) and the product standard for the equipment. The product standard requires that the type and maximum size of OCPD be on the nameplate. Where the type of OCPD shown on the nameplate is a fuse, you are only permitted to use a fuse.

I have not seen one with that marking in a long time. Typically that marking predates the HCAR breakers which have been around for at least 3 decades now. It has to do with the protection of equipment that has multiple motors, and standard breakers did not do a good job with that.

When the HCAR breakers first came out, the name plate marking would often say "fuse of HCAR breaker". Now most just say OCPD because all listed breakers are HCAR breakers.
 

jap

Senior Member
Occupation
Electrician
It gets down to 110.3(B) and the product standard for the equipment. The product standard requires that the type and maximum size of OCPD be on the nameplate. Where the type of OCPD shown on the nameplate is a fuse, you are only permitted to use a fuse.

I have not seen one with that marking in a long time. Typically that marking predates the HCAR breakers which have been around for at least 3 decades now. It has to do with the protection of equipment that has multiple motors, and standard breakers did not do a good job with that.

When the HCAR breakers first came out, the name plate marking would often say "fuse of HCAR breaker". Now most just say OCPD because all listed breakers are HCAR breakers.

I agree with others that mentioned more care needs to be put into the nameplates to indicate both the type and the max size.

JAP>
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It gets down to 110.3(B) and the product standard for the equipment. The product standard requires that the type and maximum size of OCPD be on the nameplate. Where the type of OCPD shown on the nameplate is a fuse, you are only permitted to use a fuse.
So this is a UL standard and has nothing to do with the NEC?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
So this is a UL standard and has nothing to do with the NEC?
Respectfully: With 110.3(b) involved, I don't think we can say it has "nothing to do with the NEC".
(110.3(b) is how I address the UL standard)
 