Where do you find the definition of a service mast in the nec.
I don't.
Where are you all getting your information about it having to be attached to to be considered a mast?
JAP>
Where is this definition. I don't see anything in art 100 or 230 which is were I would expect to find it if there was one.
Note 230.28 that has been quoted a couple times here is titled "230.28 Service Masts as Supports."
I have on occasion installed or run into masts used as support for other than service applications as well though NEC seems to only focus on "service masts".
we both posted at about same time, but I agree. NEC should maybe word it as raceways supporting overhead conductor runs or something of that nature, and be inclusive of all overhead conductor runs and not just service drops.Like my description earlier, is a mast on a sailboat only considered a mast when supporting the sails?
I think not, I think that long pole sticking up out of the middle of a sailboat is a mast regardless of whether the sails are up or down.
If not, it needs to be called a mast for the simple reason it sounds much cooler.
If you've installed a mast for other than service applications, why did you call it a "mast" ? out of habit ? or was there something somewhere that says the pipe you installed up in the air was definitely a "mast" ?
Why would you need to suffer the expense of a rigid conduit if it's not supporting the load of anything unless the power company requires it that is?
I agree with you all on the whole mast vs. riser thing, but, the OP was asking where does it say you cant use EMT as a service mast.
I think the better question would be, can EMT be used as a raceway for service conductors.
If the answer is yes, then there is no reason that EMT cannot be used for the raceway coming out of the top of a meter base.
At that point you would need to know if the service drop is actually going to be attaching to it or not, and, if so, then the rules for strength and support kick in.
If not used as a means of support, I don't see why EMT couldn't be used as the raceway for the service riser or mast or whatever you want to call it.
JAP>
The same rule as in 230.28, also appears in 225.17 to cover overhead runs that are not service conductors, and both sections only apply where the "mast" is being used to support conductors or cables.we both posted at about same time, but I agree. NEC should maybe word it as raceways supporting overhead conductor runs or something of that nature, and be inclusive of all overhead conductor runs and not just service drops.
A change to "raceways" would not be appropriate as there is no requirement that the supporting mast be a raceway. For example temporary services in my area most often use a 4x4 as the mast to support the overhead service conductors.
So write and submit a Public Input with a definition that will work for the application of the NEC.Another interesting take on the word mast, and, all the more reason using the word "mast" is deceiving.
Again, picturing that, the 4x4 is described as a "mast" because it's the part that's sticking up in the air.
If we are going to call a 4x4 a mast just because it supports overhead service conductors , why would that be any different than a bracket that may be built above a roof line to support an EMT "mast" above the roof, but, the service conductors were attached and supported by the bracket instead of the EMT ?
Does the bracket now magically become a "mast" just because the service conductors may have attached to it?
I say no.
JAP>
However, I expect the panel's response will be that "mast" is a commonly understood word and does not need to be defined in the NEC.
The official dictionary for the NEC for terms that are not defined in the NEC or other building codes it the Merriam_Webster Collegiate Dictionary, 11th Edition, but I don't have a cope and don't know how it is defined in that dictionary.
Yes....but it is really just a service raceway.Can EMT be used as a service mast as long as it's not used to support service conductors?
JAP>
Our family had a 45-foot sailboat (Javalin) moored in a slip in Maria Del Ray with Los Angeles Athletic Club next to the Warehouse Restaurant, we had a mast.
Any sailors out there ?
I don't see why it can't support the service the service drop, if it is strong enough to withstand the strain imposed on it, it is POCO's and some AHJ's that impose a rule requiring RMC. NEC as written just says it needs to be able to withstand the conditions.Can EMT be used as a service mast as long as it's not used to support service conductors?
JAP>
Yes it is. That drawing was around when I started in WA in 78Here is a nice graphic for longer masts. I believe this is from Washington state
EMT is not allowed in WA for service entrance conductors, Dennis posted the drawing on masts we go by
The mast would serve as a point of support for the service conductors which is above the point of attachment of the utility's service drop. The utility's service standard often requires that the point of support for service entry conductors must be above the point of attachment of the utility's supply conductors (service drop) in overhead services. If the point of attachment for the service drop, which is needed to have the clearance required between the service drop and the surface over which it passes, does not leave a higher place to locate the service head on the building that is above the Service drop point of attachment then a mast would be one way of getting the service conductors support point above that of the service drops point of attachment. This is a lot harder to describe than it would be to have a picture of it but I did my best.What would a drop be supported by if it isn't supported by the mast? What other function would a mast serve?