- NE Nebraska
- EC
Via an EGC.This permit is for a panel change out. Is your opinion this would require EGC extended from the disconnect?
AND are you stating this installation was not compliant in previous code versions?
Adds the question How is the panel case to be bonded?
Bonding the neutral is really no different than bootlegging the neutral to an EGC terminal at an existing two wire receptacle.
NEC does have some provisions for upgrading two wire receptacles and using GFCI protection. No such provisions for upgrading a feeder other than for feeders supplying separate structures that at one time were compliant bonding the neutral at the separate structure. That is one place you could still bond the neutral when replacing the panel.