Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
I’m trying to do a design for the temp wiring/power to these trailers.LOL
Trailer panels are single phase 120/208v
2 trailers with 60A main breaker panel -Might feed them with 40A. One of the trailers is ours and was told we always feed it with 40A and not a problem.
1 trailer with 125A main breaker.
I am going to have a 250A 277/480v existing panel that we will use for power that will feed a xfrmr. This xfrmr will feed sub panel. This subpanel will feed the trailers.
Working backwards.
Hope this makes some sort of sense. Thanks for the help.
Trailer panels are single phase 120/208v
2 trailers with 60A main breaker panel -Might feed them with 40A. One of the trailers is ours and was told we always feed it with 40A and not a problem.
1 trailer with 125A main breaker.
I am going to have a 250A 277/480v existing panel that we will use for power that will feed a xfrmr. This xfrmr will feed sub panel. This subpanel will feed the trailers.
Working backwards.
- The subpanel feeding the trailers can be a single phase panel, correct? I will have (1) 125A and (2) 60A branch breakers( could possibly be 40A) in the panel. What size main would I have in this subpanel. 200A?
- I could use a 75kva xfrmr as that would output 208 amps on the secondary 120/208v side?
- This xfrmr would require a 125A breaker in the existing panel to feed the 277/480v side?
Hope this makes some sort of sense. Thanks for the help.