Ricko1980
- San Francisco
- Electrical Contractor
Hi All,
I'm having a debate with a local solar installer about recoding wires for wire sizes AWG 6 or smaller. The AHJ here in San Francisco generally let us re-code 12/2 Romex into use for a 240 circuit by fully taping the accessible portion of the white wire red, thereby providing a 2-wire circuit with a red and a black only (no grounded conductor). This is for pure 240 appliances like heat pumps, which take no grounded conductor.
The solar guy is saying that this kind of tape-based coding can only be done for AWG 4 and larger. My understanding is that this is true for neutral and grounded wires, but that ungrounded conductors can be coded by tape even at a smaller size. I'm looking at 210.5(C) and 215.12(C), but maybe someone else has a better reference since these only talk about systems with more than one nominal voltage, and DC systems, and I'm looking at AC circuits, which are only mentioned in passing in the commentary to 215.12(C).
Thanks for your thoughts, I'd appreciate if someone could clarify this for me,
Ricko
Ricko