POCO's assurance that the power was on, without on-site inspection might also play a role in responsiblity, depending on when the damage actually occurred.
That is now the issue. What happened, when and why.POCO's assurance that the power was on, without on-site inspection might also play a role in responsiblity, depending on when the damage actually occurred.
I believe you are correct. The reason all the voltages looked good at the start (phase to phase - 240V, each phase to ground/neutral - 120V) is because the water main ground and rods were in place. Even if a POCO rep actually did come out to the home and checked across the meter he would have gotten the same readings until something turned on. The HO was away and just about everything was off except the fridge, forced hot air heat and the gas water heater. After checking, the fridge is working but I left a note to discard EVERYTHING in the it. The heat comes on, flame ignites but the blower doesn't come on. The water heater doesn't work. There's an electronic control on it that I'm sure got toasted. There was a smell of burnt eletronics in his office and I'm hoping that his battery back-up burnt up and not his 2 computers.Interesting and worth noting that the AFCIs tripped in this situation. I would not have assumed that would happen. (Nor would I assume it would always happen.)
To me the biggest lesson and theoretical point here is that just because voltages look fine with no current flowing does not mean all will stay well when you turn on load. A 'good ground' can make the neutral look okay when it's not. Not sure of a quick or easy way to catch this (other than visual inspection might be obvious).
I believe you are correct. Kind of like the self-destruct feature in Mission Impossible.Sounds to me that without the neutral, the AFCI breakers saw 240 on their electronics through the pigtail and destructed.
-Hal
I agree that you are not likely to get any money from the power company.POCOs here approach it as no negligence on their part. The tree falling was "an act of God" (or nature if you prefer).
Feel free to sue mother nature.
John Clarke and Don Watson might have an answer.POCOs here approach it as no negligence on their part. The tree falling was "an act of God" (or nature if you prefer).
Feel free to sue mother nature.
There have been real life lawsuits attempts against God as well.John Clarke and Don Watson might have an answer.
![]()
The Man Who Sued God - Wikipedia
en.wikipedia.org
I've noticed this myself.A lot of modern power supplies for computers, TVs, etc. are the universal type (100V-240V) so wouldn't be damaged.
But not quite universal enough to be connected to a 277 circuit.A lot of modern power supplies for computers, TVs, etc. are the universal type (100V-240V) ...
Wasn't the issue a broken neutral on a 240/120V split phase service? 240V would be the maximum that anything would see.But not quite universal enough to be connected to a 277 circuit.
The ones I've seen aren't rated any higher than 265 actual volts, leading to the creation of yet another kludge, the 416Y240 service for massively multiplayer data farms.
That's 120/240 split phase to you.Wasn't the issue a broken neutral on a 240/120V split phase service? 240V would be the maximum that anything would see.
Wasn't the issue a broken neutral on a 240/120V split phase service? 240V would be the maximum that anything would see.
I think I have it remembered, then this pops up again.That's 120/240 split phase to you.![]()
Universal in this case means the same item will work on a typical 120 volt circuit in North America or on a typical 240 volt circuit in many other countries.But not quite universal enough to be connected to a 277 circuit.
The ones I've seen aren't rated any higher than 265 actual volts, leading to the creation of yet another kludge, the 416Y240 service for massively multiplayer data farms.