sgtsparky
- Dexter, Oregon, USA
Looking for assistance: with new construction. I always use metal boxes for commercial construction (+3 story's)
I am currently working for a medical center with a Highrise and found plastic low voltage rings (old work style, 2 different brands).
I do not believe these are legal however I cannot find a code reference.
The building is class 1 fire restive, so I do not believe the low voltage rings (not a box) should be allowed in the building at all.
One of the contractors told me they don't use them in the 1- or 2-hour fire walls but do use them in some areas.
The UL listing says 0 hours fire rated. I have searched NFPA 70 ,99 & 101 but have not found a allowance to use them or not to use them i am especially concerned with patient areas. Anyone have a code reff ? structural building or electrical. I still plan on using metal handy boxes with battleships as that was specified.
I am concerned with the rings in use and the director asked what code do they violate? the carlon SC100RR UL listing E216492 was no help i did not look up the arlington LV2 rings, might try today.