What wire and breaker needed?

Status
Not open for further replies.

olly

Senior Member
Location
Berthoud, Colorado
Occupation
Master Electrician
I have a infrared sauna I am going to hook up. I cant get the manufacture to give me the specs as far as recommended breaker size. It pulls 47.5A.
They said to put it on a 47.5A breaker and use 8/3 HAHAHA

This should get a 60A breaker with 6/3 CU since I am using NM cable. Correct?
 
I’m with you! Can you pull up anything online using manufacture and model number? I would think that it is a continuous load 80% of 60 is 48 amps. Or 47.5/.8 v 59.4 amps or 60 amp breaker!
 
Would not expect a sauna to be a continuous load, as it cycles on and off once up to temp and most people don't sauna for 3 hours unless this is some group situation with people always going in and out. Would think #6 NM on a 50A breaker is fine.

Is this cord and plug connected? That should provide some clue as to true load and if a neutral is needed.
 
I agree probably not a continuous load so a minimum 50 amp branch circuit.
 
I agree probably not a continuous load so a minimum 50 amp branch circuit.
So can I use #8 CU NM cable considering 240.4 B on a 50A breaker? I get confused with, you have to use the 60 degree column when using NM and how 240.4 B comes into play - you can use the next higher standard over current device .
I would think the answer is no you cannot use #8 CU that = 40A in the 60* column, since the next standard ampere breaker would be a 45A. Correct?
I have a guy that is telling me you can use #8 CU in NM cable for a 50A breaker.
 
Last edited:
I would think the answer is no you cannot use #8 CU that = 40A in the 60* column, since the next standard ampere breaker would be a 45A. Correct?
I have a guy that is telling me you can use #8 CU in NM cable for a 50A breaker.

#8 NM cable at 60° C is 40 amps so there is no next size up since 40 amps is a standard size. You can protect #8 MC cable at the 75° C ampacity of 50 amps because there is no 60° C limit on MC cable.
 
#8 NM cable at 60° C is 40 amps so there is no next size up since 40 amps is a standard size. You can protect #8 MC cable at the 75° C ampacity of 50 amps because there is no 60° C limit on MC cable.
And you can't protect #6 NM at 60 amps for this either.
 
Don’t forget to factor in the distance from the panel to the hot tub, it might require de-rating to avoid a significant voltage drop. Ending up with low voltage at the tub can affect the pump motors.
 
So can I use #8 CU NM cable considering 240.4 B on a 50A breaker? I get confused with, you have to use the 60 degree column when using NM and how 240.4 B comes into play - you can use the next higher standard over current device .
I would think the answer is no you cannot use #8 CU that = 40A in the 60* column, since the next standard ampere breaker would be a 45A. Correct?
I have a guy that is telling me you can use #8 CU in NM cable for a 50A breaker.
And you can't protect #6 NM at 60 amps for this either.
I would do what Infinity stated by using MC, in which, #8 at the 75 column is good for 55 Amps, as long the terminals are rated for 75 C but it could come down to cost
 
What about the connections at the sauna? Lugs? Temp. rating?
 
What about the connections at the sauna? Lugs? Temp. rating?
You're correct that the terminals need to be considered but IMO we've come to the point where just about everything is 75°C and it's safe to assume so. If this were a test question then that would change the conversation.
 