I have a infrared sauna I am going to hook up. I cant get the manufacture to give me the specs as far as recommended breaker size. It pulls 47.5A.
They said to put it on a 47.5A breaker and use 8/3 HAHAHA
This should get a 60A breaker with 6/3 CU since I am using NM cable. Correct?
They said to put it on a 47.5A breaker and use 8/3 HAHAHA
This should get a 60A breaker with 6/3 CU since I am using NM cable. Correct?