Yes.Can the integral photocell within the fixture be ‘bypassed’ if desired in order to utilize an external photocell
Please surf the web. Key words: "contactor", "inrush VA"Nice to know.
Where did you find the info on inrush and sealed VA? Thanks
Sounds like a good reason to not energize them all at olne time as a single group.
I worked an interesting problem about 2 years ago involving 6 small LEDs on an electric tugger we were building, all run on 24 VDC. I will someday create a post about it, and the troubles I encountered with welded relay contacts. But to post here briefly, see the screenshot below for how high (and fast) the current can be when the LEDs were turned on. Charging up the empty DC capacitors in the LED, with little or no current limiting circuitry, is like a dead short / black hole / Scotty, give me everything you can problem.Read up about the inrush of LED lights. For a half a cycle or so, it is extremely high. I don't have time the research it again now, but I remember that it can be hundreds of amps.
For reference, the steady state draw after turning on was ~3 amps. But that peak draw was ~140 amps when the contacts closed!! It's all over inside 1 msec. Then the current draw drops to almost zero as the thing gets ready to turn on, which it does after about 10 msec.
Again, this was for a DC device, but the same peak current problem exists in the AC world for sure. And it can cause real problems at switch-on.
So what you’re saying is the inrush was really no factor at 1msec