Strathead
- Ocala, Florida, USA
- Electrician/Estimator/Project Manager/Superintendent
We have an engineered system. The project is a new be tower for a hospital, so the need is supplying the emergency system from the generation plant (CEP). It steps the voltage up from 480 to 4160 and back down to 480/277 a few hundred feet away. There are some inconsistencies. Note that both transformers and all interconnection wiring is outside.
The drawings show, a Wye/Wye step up and a Delta/Wye step down. See the attached drawing. Square D supplied a step up transformer that they describe as 4160GY/2400 primary 480 Delta secondary (which is obviously reversed in terms), and a step down of 4160 delta to 480Y/277 secondary. Not what the drawings show.
All that said, regardless of what is on the one line, what is required for wiring?
First, feeding the primary of the step up. Did it need a neutral as shown if the primary was Wye and why?
Next does the secondary require the common point (neutral) to be grounded to a grounding electrode system as shown?
Does the interconnection require the ground to be pulled between them and if so, what is the code section? Also please explain why it is or isn't required.
Any speculation on why the engineer drew is one way, and Square D submitted it another way, which the engineer didn't reject.