If they can beef up breakers just for EV and PV systemsI'm all for it. I have on my iPod lot of pictures of burnt up circuit breakers that were feeding one or the other of the two I mention. Contractors put in #2 cu conductors to Tesla wall chargers and the 100amp breakers feeding melted. Checked connections and all were spec or tighter. And now Tesla doesn't sell 100 amp chargers any longer so I'm feeling fairly certain it must have been more than just the ones I have looked at. Not as often I have seen similar cases with grid tied PV installs but on those , I am not convinced that the connections at the branch circuit breaker were properly torqued. I found very loose connections at breaker terminal lugs on more than one case I have investigated .