Having this office debate about how to properly calculate the voltage drop of a street lighting circuit for line to neutral circuits on 3 phase systems.
System info:
Formulas use to calculate voltage drop:
Option A:
V drop = 2 * I * R * L
I = current
R = resistance per 1000’
L = one way length from source to load, “2” doubles this for round trip length since it’s single phase.
Vdrop = 4.57 volts or 1.65% (assuming #10 AWG wires at .95 PF)
Option B:
V drop = I * R * L
Vdrop = 2.28 volts or .82% (assuming #10 AWG wires at .95 PF)
Looking at Table 9 in the NEC and the subsequent examples, it’s not any clearer (to me)
Note 2 under Table 9 indicates “Multiplying current by effective impedance gives a good approximation for line-to-neutral voltage drop”
If I simply do I * Zeff (effective impedance) as it states, on the above equation it’s without the “2” and V drop = I * R * L like in Option B. Unless there is something else not explicitly state to consider.
Now in a balanced 3 pole circuit, 3Phase, 4 Wire circuit, with 10 lights per phase (30 total), I can understand there being ~0 current on the neutral wire since the three phases are out of phase by 120° , offset each other and sum to 0. In that instance I would remove the “2” from the equation above since it’s only the source to the load distances that would have voltage drop.
Couldn’t really find definitive answers one way or another on the internet on how to truly calculate this voltage drop. Obviously there's a large difference in voltage drop as the quantity of fixtures get larger and farther apart - it effects wire size, conduit fill, and ultimately cost for the owner so it's important to get right!
System info:
- The power system is 480Y/277V, 3 Phase.
- The branch circuits for the various lighting circuits are 20A, 1 pole breakers running line, dedicated neutral, and ground out to each fixture in the circuit, with an average of 10 fixtures per circuit.
- The light fixtures themselves are 277V @ 100VA each and are spaced out 100’ apart
Option A:
I = current
Option B:
V drop = I * R * L