In a sub-panel, our company originally had one branch circuit from one phase powering 4 parallel receptacles. Since this is outdoors, the first receptacle connected to line was a GFCI. The load side of the GFCI fed all other single gang receptacles as normal.
However, soon after company diesels were plugged in for heating motors over night, and soon increasing the number of vehicles, the standard GFCI overheated and blackened.
In order to increase total ampacity of 4 receptacles, another coworker, while I was off work fed a separate red wire from the other phase from the same panel to split receptacle into two groups. Which is ok.
What he did not do was run a separate neutral for the two pair of receptacles nor a separate equipment ground conductor
As a result two separate circuits shared a neutral which I believe defeats the purpose of having another line wire added since double amps from 4 receptacles return on one neutral as it did in original setup.
Also is NEC 200.4 which took me a while to find. Co worker said installing a separate neutral and ground was not necessary? What do you all think?
![FB_IMG_1680786263313[1].jpg FB_IMG_1680786263313[1].jpg](https://forums.mikeholt.com/data/attachments/28/28429-9f6df0835414b50964452c7cc8b9d787.jpg)