jaggedben
- Northern California
- Solar and Energy Storage Installer
Retire
The plug adapter on the Tesla EVSE tells it what the rating of the plug is. The 14-50 adapter therefore tells the cable that more current is available than the plug adapters for lower rated receptacles. (The Tesla cable with the built-in box performs the same function as a wall-hung EVSE here).
But again, all this is not to blame for receptacles melting. The circuit breaker should trip to protect the receptacle no matter what load is plugged into it. Melted receptacles is due to either a receptacle not performing to its purported rating, a breaker not tripping when it should, or a wiring error causing excess heat at the receptacle when under acceptable load.
if charging is done based on a simple cord equipped with a 1450 plug on one end and a Tesla charging handle on the other end, plugged into a 1450 receptacle, i don't see how the charging rate can be set automatically. ...