Alwayslearningelec
- NJ
- Estimator
Since it says to install new fused disconnect I'm not sure how you came to that conclusion.Looks to me like they want you to use the existing fused switch or breaker to feed your VFD'S and do away with the NEMA starters
Sent from my SM-S134DL using Tapatalk
Generally, “spare” means a spare starter or feeder, if it is empty, it’s usually referred to as a “space”. But of course, that is not a hard and fast rule, I too have seen the word “spare” used to refer to a space (but not the reverse).The correct way is to remove the existing buckets and replace them with new buckets that you get from the MCC manufacturer.
Spare just means it's unused. It might be empty, it might have an unused starter in it. In either case the correct fix is to pull the existing buckets out and replace them with what the customer wants now.
They clearly say to install NEW fused switch.`Looks to me like they want you to use the existing fused switch or breaker to feed your VFD'S and do away with the NEMA starters
Two of them point to the starter symbol and say to remove that, implying that they want to re-use the fused disconnect in the starter bucket. But you are right, the lower left note says to provide new switches.Since it says to install new fused disconnect I'm not sure how you came to that conclusion.
Looks like the starter is totally removed, and wire is ran directly to the vfd from the new disconnect.The starter just gets line/load 600v wiring?