The electron man
 - Nyc
 - Electrician
What's the best solution to protecting outlets with no ground , I was looking into it and what I found was the solution is to put a gfci, but would  a gfci work without a ground ??
			Because the source neutral is grounded. The circuit EGC has nothing to do with GFCI operation.
By the utility and by the premises grounding-electrode system.1 . How's is the source neutral grounded
One will protect those fed from the load terminals.2. would I have to put a gfci in each ungrounded outlet or will one protect the whole circuit
Absolutely.3. If not could I just put in a gfci breaker ?
Back at the service and throughout the utility. Else why would you get a shock when you contact a hot and something connected to ground like a water pipe?. How's is the source neutral grounded
Either or.
You could.
-Hal
So it will only protect the down stream right?By the utility and by the premises grounding-electrode system.
Absolutely.
Absolutely. The only difference is the absent individual circuit EGCs.But in old homes with no ground there is still bounding ?
Absolutely again. It has to monitor the current in the circuit conductors.So it will only protect the down stream right?
Honestly I wouldn't worry about it for most residential outlets as most general resi stuff doesn't have three prong plugs anyway.What's the best solution to protecting outlets with no ground , I was looking into it and what I found was the solution is to put a gfci, but would a gfci work without a ground ??
Got it thanks againAbsolutely. The only difference is the absent individual circuit EGCs.
Always good to check it was done right. (I've seen a few that weren't.) But the way it is supposed to be done hasn't changed in any important way for at least a hundred years.But in old homes with no ground there is still bounding ?
Not only downstream, but at the GFCI receptacle as well!Absolutely again. It has to monitor the current in the circuit conductors.
In that sense, it's a "series" device (like a switch or fuse), not a "parallel" device (like a surge protector).
Of course.Not only downstream, but at the GFCI receptacle as well!
What do you mean all the gfci receptacles as well, those protect themselves since they are gfciNot only downstream, but at the GFCI receptacle as well!
Several times have left 2-prongs and ran new circuits to provide a 3-prong ea roomHonestly I wouldn't worry about it for most residential outlets as most general resi stuff doesn't have three prong plugs anyway.