Wood inside of a junction box

Status
Not open for further replies.
Hoffman offers plywood back panels. Just saying.


Sent from my iPhone using Tapatalk
Augie was ahead of me on this. Common for telephone. Back in the day I would look in the Hoffman catalog to see about the details and listing data, but no more catalogs for me.
 
Last edited:
I have seen three phase utility CT cabinets with wooden backplates.
 
There is a difference between a wireway which does not come with the wood back option and a CT can which may have. The issue is that the terminal blocks inside the wire we are required to have insulating covers as pointed out in the second post.
I don’t know if a CT can with a wood backboard is allowed by the NEC, as often the CT scan requirements are dictated by the power utility.
 
Now where will I find that, it's not in article 100 of the NEC.............. I checked....
They have their own article, 366. I will defend your use of the word "gutter" because that is common jargon for a wireway and usually not meant to refer to an actual "auxiliary gutter". Just like when we say THHN, we typically don't mean actual THHN that is dry location only.
 
But I didn't say Auxillary . Not even once. Wanna know what else? I've read Chapter 3 at least 500 times over, since I got done with Vocational school back in 1976. If I meant " Auxillary Gutter", I would have said that. But I meant what I said cause that is the name which I can always buy that exact "thingamajig" showing in the picture at the wholesale houses, both here and in several cities in Florida I have worked in. I ask for a gutter and I get a " Wireway". Sometimes I ask for Romex and I get NM cable. But calling a six foot by 24" Gutter a junction box is something an electrical engineer might do, but just about never an electrician. Anyway, that picture is going to ruin my Alaska vacation now that I know how they splice things up there.........
 