It sounds like the NEC would call these optional standby systems not 'emergency' or backup units. Again a common language with multiple meanings per word gets us into trouble.The NEC does not cover Temporary Emergency Generators. We use various connection points on a building or structure. The neutral is not switched and a transfer switch is not used.
Thoughts about if a grounding electrode is needed?
Agree. FEMA terminology is not code terminology. But being out installing generators those without power understand emergency generatorIt sounds like the NEC would call these optional standby systems not 'emergency' or backup units. Again a common language with multiple meanings per word gets us into trouble.
OP states that there is no ECG. If the neutral is bonded to ground at the generator as OP states, then the neutral needs to be switched.Per the OP he does not have an SDS so his generator is connected to the building grounding electrode system.
The NEC only applies to 'installations'. To the extent 'temporary' means 'not installed', the NEC may not apply. For example in my opinion the NEC does not apply to cord and plug connected portable generators.where does it say in the code that temporary generator installations are exempt from the code?
Maybe not the genset itself (governed by multiple UL standards), but how it connects into the permanent structure wiring NEC does apply. It also applies to the NG bonding at the Genset related to interconnection with existing buildings electrical system. In most instances, NG bonding not acceptable for "portable" generators connected into a building system (SDS exception separate rules).The NEC only applies to 'installations'. To the extent 'temporary' means 'not installed', the NEC may not apply. For example in my opinion the NEC does not apply to cord and plug connected portable generators.
Only go around is that it never gets connected into the existing building, multiple extension cords to individual corded appliances.That said, it seems like the OP is doing work which, however temporary it may be, rises to the level of installation, in the sense that it goes beyond just moving things around and plugging them in.
Look at 700.3(F) Temporary Source of Power for Maintenance or Repair of the Alternate Source of Power.The NEC does not cover Temporary Emergency Generators. We use various connection points on a building or structure. The neutral is not switched and a transfer switch is not used.
Then I see the only compliant means would be individual appliances connected via a cord, not tying into the building electrical system, OR treat as an SDS and all its requirements.Our generators are bonded and so are the buildings main disconnects, so if we have a neutral we don't install a EGC for obvious reasons. These installations are not code compliant.
Right but that arguably can't include requiring a grounding electrode for a temporarily positioned portable cord and plug connected generator. Nor does the NEC attempt to require this anywhere, to my knowledge.Maybe not the genset itself (governed by multiple UL standards), but how it connects into the permanent structure wiring NEC does apply. ...
Ok so I read back and apparently the gensets are NG bonded, so EGC is a parallel path for neutral currents. I guess you don't want to drive a ground rod because these things are sitting on pavement or concrete?
I don't know these specific gensets, but some of the larger ones I've worked with lifting the N-G bond was no big dealHe said they don't install an EGC because the neutral is bonded at generator. Post #20.
No wire, no parallel path.