590.1 Scope. The provisions of this article apply to temporary electric power and lighting installations.
590.2 All Wiring Installations.
(A) Other Articles. Except as specifically modified in this article, all other requirements of this Code for permanent wiring shall apply to temporary wiring installations.
However 525 is not clear that a grounding electrode for the portable structure is not required. If that article does not modify the requirement in Article 250, 250 will apply.Is the panel hard wired into a power source? Or is it portable and fed with 50 amp CS or camlock? I do alot of tent power and we use portable distribution boxes, following the applicable portions of nec 525. 590 doesn't come into play since this is 'portable' not 'temporary' but if hard wired then 590 would.
525.30 Equipment Bonding.
The following equipment connected to the same source shall be bonded:
(1) Metal raceways and metal-sheathed cable
(2) Metal enclosures of electrical equipment
(3) Metal frames and metal parts of portable structures, trailers, trucks, or other equipment that contain or support electrical equipment
(4) Grounding electrodes or connections to a grounding electrode shall not be required
Where the metal frames or parts of the equipment in 525.30(1), (2), or (3) are likely to become energized in the event of a fault, the equipment grounding conductor of the supply circuit shall be permitted to serve as the bonding means.
While we don't do that, what says we don't have to have a GES for the construction trailer?Presuming this is truly a freestanding item then if you had a trailer, say like many construction guys have with a 50 amp supply cord, panel and multiple receptacles on/within the trailer - electrically you basically have the same thing but that doesn't require a GES at the trailer/panel.
Good question, I looked some, haven't found a definite answer yet.While we don't do that, what says we don't have to have a GES for the construction trailer?
The construction trailers are covered by Article 545 now and there is no clear statement as to requiring a grounding electrode system, but there is a clear statement requiring provisions for the connection of a GECGood question, I looked some, haven't found a definite answer yet.
I will say they almost never have a GES connected to the trailer. Often might have one on/very close that is serving whatever equipment they are supplied from. But if you ran say a hundred feet to a individual receptacle on some post, I don't believe a GES is required for that receptacle, and I really doubt the trailer would require one either, at least not by NEC alone.
545.12 Grounding Electrode Conductor.
Provisions shall be made to route a grounding electrode conductor from the service, feeder, or branch-circuit supply to the point of attachment to the grounding electrode.
The OP said this was for a wedding tent. If you can't talk her into marrying you in 90 days, might as well give up!For something like that, I wouldn't install a rod.
A couple or three spider boxes would do the job and be a lot easier to handle (use 6/4 SO cable to feed them). If you're constantly moving this thing, when it wears out get some purpose-made temp. power equipment.
Be aware of the 90 day rule in Art 590.3, depending on how you read it, it may not directly apply. I know it's been discussed before.
I agree. This is used only for the 5 hrs or so during the day of wedding.For something like that, I wouldn't install a rod.
Flip that- what is there to say that 2 rods are required? That's more important.So apparently from what I gather, there is nothing to cite to the AHJ regarding not having to drive 2 Gr Rods.
PORTABLE equipment (and alot of jurisdictions are requiring it be listed nowdays -UL1640 is the standard)That's a lot easier if it's all cord & plug connected using purpose-built temp power equipment.