My understanding is the Enhanced Content is suppose to help clarify some aspect of the code. Maybe.
enhanced content from 2023- 705.12(B) explanation:
ENHANCED CONTENT
The required ampacity of a feeder or bus connected to the interactive inverter is based on the inverter output circuit current, rather than on the overcurrent protective device (OCPD) in the inverter. Except where 705.12(A)(2)(b) and (B)(3) apply, the required conductor ampacity is determined by adding the ampacity of the primary OCPD protecting a busbar or feeder and 125 percent of inverter output current.
Where a tap is made to a feeder supplied by the inverter and the normal source, the calculated sum is used as the rating of the overcurrent device to determine the ampacity of the tap conductors in 240.21(B).
Unlike in service equipment where the number or rating of overcurrent devices is not limited, 705.12(B)(3) places a limit on panelboard overcurrent devices. The sum of the ratings of all overcurrent devices (excluding the main overcurrent device) supplying and/or being supplied by the panelboard is limited to the busbar rating. In addition, the main overcurrent device also must be limited to the ampacity of the busbar.

IMAGE
NFPA70 705.12 enhanced content
enhanced content from 2023- 705.12(B) explanation:
ENHANCED CONTENT
The required ampacity of a feeder or bus connected to the interactive inverter is based on the inverter output circuit current, rather than on the overcurrent protective device (OCPD) in the inverter. Except where 705.12(A)(2)(b) and (B)(3) apply, the required conductor ampacity is determined by adding the ampacity of the primary OCPD protecting a busbar or feeder and 125 percent of inverter output current.
Where a tap is made to a feeder supplied by the inverter and the normal source, the calculated sum is used as the rating of the overcurrent device to determine the ampacity of the tap conductors in 240.21(B).
Unlike in service equipment where the number or rating of overcurrent devices is not limited, 705.12(B)(3) places a limit on panelboard overcurrent devices. The sum of the ratings of all overcurrent devices (excluding the main overcurrent device) supplying and/or being supplied by the panelboard is limited to the busbar rating. In addition, the main overcurrent device also must be limited to the ampacity of the busbar.