MisterMoSparky
- WV
- Residential Service Electrician
Currently this homeowner has a 200A panel in their basement with a 50A breaker supplying power to a Subpanel in the garage. Whoever ran wire to garage in the past did not provide an equipment ground. They only provided an SER cable with 2 insulated hots and a bare uninsulated neutral. Several questions, if homeowner does not plan on having 240V loads in garage would it be okay to simply put 1 insulated conductor as a hot, the second insulated conductor as a neutral, and the uninsulated conductor as an equipment ground, all on a 50A GFCI breaker. Will breaker preform properly with only one pole of breaker and neutral being used. Additionally let’s say homeowner does want a 240v load out in garage. GFCI protection can be used in lieu of an equipment ground but will the uninsulated neutral wire cause issues with leakage and nuisance tripping. Also if no equipment ground is provided to the garage do I need to supply a grounding electrode outside of the garage to protect equipment inside Subpanel?