jaggedben
- Northern California
- Solar and Energy Storage Installer
So what would it take to get 18 gauge communication wire in the same existing conduit as 40A 240V power delivery?
You could try making your own twisted pair with class 1 conductors. (See discussion in that thread.) Hopefully interference isn't a problem.
I agree with Larry and others that the meter which takes the CT secondaries as input and outputs the RS-485 should not be in the panel. The proper location would be a j-box adjacent to the panel. The RS-485 could leave by a different direction and rejoin the 40A EV circuits in a T-condulet.
I just told you. A cable rated at 600V! You said you had a source for it didn't you?
I believe it either has to be listed by the manufacturer or Class 1 conductors. For example there is Cat6 with an outer 600V jacket, but that's not code compliant unless listed. I believe it will work fine, and I've used it with high voltage DC with manufacturers blessing (although in retrospect, I'm a bit skeptical they got it listed).