jaggedben
- Northern California
- Solar and Energy Storage Installer
So this one is almost certainly code compliant (see Wayne's last post). But I'm unclear if it gives you the twisted pair you need for RS-485? (You need at least one twisted pair, right? That's my experience but I've only used RS-485 in a couple applications.)Would this be suitable?
https://www.wireandcableyourway.com...tation-cable-w-overall-shield-type-tc-er-600v
18/1PR Type TC, Tray Cable, Overall Shield, 600V
Permitted use in Class 1, Division 2 industrial hazardous locations per NEC. Listed Type TC.
Rated at 90°C dry, 75°C wet
Any corrections to this code citation? Under 2020 NEC 725.48:
These do not appear to have NEC recognized ratings and would not be compliant.