ruxton.stanislaw Spammer
Suspended Member
- Arkansas
- Laboratory Engineer
One potential fix for this, if the manufacturer supports it, could be to rectify the input current. I expect an isolation transformer would also help.
Based on the physical layout described by the OP, feeding the mat from a balanced source should indeed cancel out the capacitive voltage/current on the outside surface of the mat. But the effectiveness of that would be less as the spacing between the rails is increased. OP did not state the spacing.
Heaters are 208 vac rated and installed on an EPDM Roof with adhesive.
2-pole 208 vac GFEPD (30 ma GF Trip) Circuit Breaker.
Would the current be below the 30 ma GF trip level? I was on the phone with EC and he said when mats are energized they all eventually trip the GFEPD.
I would not presume that. A metal roof structure on masonry walls will be pretty effectively insulated from ground after the concrete & mortar are fully cured. New construction? What kind of construction?Is there a metallic roof underneath the EPDM membrane? ... which is presumed to be grounded. ...
The EC did say that they were using the T-stat to break two hot legs from two Circuit breakers. I advised him not to do this.
EC said that there was no leakage prior to energizing the CB's. ...
When a meter is used, it is measuring 110 vac to ground on the outside of the mat (a t-stat is breaking one hot leg of the circuit when not calling for heat). When the T-stat calls for heat, the voltage to ground drops by 50% to 55 Vac.
Is there a metallic roof underneath the EPDM membrane? If so, there will be some capacitance between the heating structures (flat bus wires and resistive elements) and the metal roof... The common mode voltage present on the 208V lines will produce a common-mode current through this capacitance. Whether that could trip a 30mA GFPE would depend on the capacitance.
The worst case is when only one of the lines to the heaters is switched off, because the common mode voltage would be 120V. With both lines switched on, the common-mode voltage from 2 phases of a 208V system would be 60V as was described earlier.
Is the breaker tripping now?...I missed that part.I think a first priority would be to use a contactor or other means to break both legs of the 208V. When only one leg is broken to turn the heaters off, the common mode voltage to the mats (and therefore the common mode current from capacitance assuming it's symmetrical on both legs) will be 2X what it'll be when the heaters are turned ON. After a contactor is in place you can see if the GFEP breaker will then hold.
Mats are on GFEPD CB's (30 ma trip). No tripping.
Exactly. But the topic under consideration at the time I posted my comment was whether adding a transformer to provided a balanced voltage would be a possible fix for the OP's problem.But these mat are _not_ being fed by a balanced source. They are being fed with 208V and as described this is single phase. The neutral point between the two hot legs is at 60V relative to ground.
Going back to slightly conductive EPDM; I wonder if a grounded conductive EPDM mat would solve this issue.
-Jon
I purchased a 2' x 3' mat (same construction) from a different manufacturer. Brought it to the site, wired it to one of the circuits (all of the three remaining CB's were turned off). I am getting the same result;But these mat are _not_ being fed by a balanced source. They are being fed with 208V and as described this is single phase. The neutral point between the two hot legs is at 60V relative to ground.
As I see it, there are several possibilities.
1) A mechanical defect or installation error that creates an actual hole in the insulating material. You are getting direct conduction through this hole, either electrons flowing through conductive material, or ions moving in the water. This is very unlikely given 2 sets of mats used.
2) A defect in the materials used to construct the mats. Both polyethylene and EPDM are generally insulators, but can be processed or 'doped' to make them slightly conductive. This is sometimes done for things such as static control, or could be caused by an unintentional contaminant, Perhaps an incorrect batch of materials was used by the mat manufacturer, and all the mats have exactly the same leakage current defect.
3) Capacitive coupling. Capacitive coupling is _always_ present when you have AC circuits. @synchro described this quite well. If you have electrodes inside the mat at 60-120V relative to ground, and an electrode outside of the mat connected to ground, you _will_ get some current flow, even if the mat insulation is _perfect_. Think about how the 'non-contact voltage sensing pens' work.
IMHO the manufacturer needs to do some megger testing to determine if there is an actual conductive defect. If there isn't an actual conductive defect, then you will need to do more investigation to figure out why capacitive coupling is evident in this installation but not in all of the other installations.
I have a _guess_: that the other installations are on grounded conductive surfaces, which provides a capacitive path to 'shunt' the capacitive leakage, or the other installations don't have a nearby metal guard rail that someone touched, and so the capacitive leakage is present but has not been noticed.
A useful additional measurement would be a low impedance voltage measurement between mat surface and grounded metal, and if the low impedance measurements shows a low voltage, then the next measurement I would make is current (amps) to ground from a region on the mat (say a 1 square foot area) to ground.
-Jon
I purchased a 2' x 3' mat (same construction) from a different manufacturer. Brought it to the site, wired it to one of the circuits (all of the three remaining CB's were turned off). I am getting the same result;Is there a metallic roof underneath the EPDM membrane? If so, there will be some capacitance between the heating structures (flat bus wires and resistive elements) and the metal roof, which is presumed to be grounded. The common mode voltage present on the 208V lines will produce a common-mode current through this capacitance. Whether that could trip a 30mA GFPE would depend on the capacitance.
A suggestion is to disconnect the heaters from both phases, and measure the capacitance from one of the lines to the metal building structure and/or an equipment grounding conductor. The other line to the heaters should be left open, or the two lines can be connected together (it shouldn't matter if only tens of milliamps are flowing). Many handheld meters can measure capacitance.
The amount of capacitance needed to draw 30mA when 120V 60Hz is applied across it is 0.66 μF (660 nF).
60Vac would require twice that capacitance to draw 30mA.
You could also measure the resistance to ground while you're at it, although this will not be applying any voltage stress to the insulation. You may have to wait for the reading to settle down because of the capacitance.
Building roof is EPDMI think a first priority would be to use a contactor or other means to break both legs of the 208V. When only one leg is broken to turn the heaters off, the common mode voltage to the mats (and therefore the common mode current from capacitance assuming it's symmetrical on both legs) will be 2X what it'll be when the heaters are turned ON. After a contactor is in place you can see if the GFEP breaker will then hold.
The T-stat is a snow control switch, DS-9, mfg by ASE Colorado, the instruction manual clearly states that it can be used to Control two Circuits fed from two CB's. The contactor has two isolated poles that would be used to "break" one hot leg from two different CB's.These statements don't add up to me. Find a different Electrical Contractor?
1. Powered at 208 vac, the dry mat is tested to ground and voltage is 2v.
2. When water is poured onto the mat, depending on the depth of the water, I was getting 50 v to ground when powered, and 110 v when I disconnected one leg of the power.
Both the replacement mats and the new test mat were manufactured with a ground covering the heating element.
I meggared the mat (at 1000v) from the bus-wires to building ground: Result 2.2G ohms
I meggared the mat (at 1000v) from the mat ground wire to building ground: Result 2.2 G ohms.
These results indicate that the insulation is intact.
I tested the mat in three location:
1. laying on the surface of the roof (EPDM)
2. We held the mat in the air (not touching any part of the building).
3. On ground Floor of Building outside on concrete
4. Inside on a wooden workbench at my EC's shop
The results for each area are the same
Did not measure current readings from mat to ground, too low as the GFEPD Circuit Breaker would trip in excess of 30 ma.
I am doubtful that the original set of mats, the replacement set of mats and the new mat from an entirely different manufacturer are defective.
Manufacturer recommended controls that open both legs of the 208 vac circuit when not calling for heat, and also switching the GFEPD CB's to standard CB's, since voltage to ground when energized is less than 50 v.
I need to check NEC code for this application to see if GFEPD is required for portable snow mats.
I think I am leaning toward some sort of capacitance occuring. If this is the case, is there any way to eliminate this phenomenon?
Thanks for the input