Jpflex
Electrician big leagues
- Victorville
- Electrician commercial and residential
We have a 3 phase delta 480 volt to 208Y/120
30KVA transformer supplying a single phase panel
To determine primary and secondary conductor sizes all terminating at 75 degrees celcius and using THHN:
When calculating delta 3 phase primary current I obviously get 30,000 VA x 480 V x 1.732 = 36.08 amperes
If I calculate the output secondary current for the 3 phase Y output I get 30,000 / 208 x 1.732 = 83.31 amperes
However, supplying a single phase panel with just 2 legs of the Y secondary becomes single phase and mathematically appears to produce more current then when using all 3 legs of the Y because 1.732 is factored into the equation.
Now when using the single phase formula to determine secondary current, the 2 legs of Y windings magically appears to increase beyond what the 3 legs of the 3 phase Y could produce. Which makes no sense
30,000 VA / 208 V = 144.23 amperes (single phase)
Vs
30,000 VA / 208 V x 1.732 = 83.21 amperes ( 3 phase all legs used in Y
If i calculate secondary conductor size for 3 phase at 1.25 % of amperes using 30,000 / 208 x 1.732 I’ll use a # 2 AWG THHN at 75 deg c. (110 amperes)
However if I calculate secondary conductor size as it is single phase at 1.25% (just A and B phases used) I use a 3/0 AWG THHN at 75 degree c (200 amperes)?
So do I size secondary conductors and OCPD to 110 amperes or 200 amperes? And would wire sizes plus OCPD be correct?
Vs