herding_cats
- Kansas
- Mechanical Engineer
Yes it’s a huge bridge rectifier
He mentiuoned: 1,600,000 divided by 480 = 3333.33 amps has to be single phase amps.How do you know that? I assume it is a three phase bridge rectifier.
Without derating etc. Not much voltage drop. Short distance.
The demand charge is the issue here with grid connection. If you pull that kind of demand, even just 1 time, you are stuck with the demand charge for the next 11 months. We’re talking about 1 charger here. So because of the low volume of trucks, it’s impossibly expensive to charge a low volume of trucks.
Oh right of course, sorry I glanced over that part of itHe mentiuoned: 1,600,000 divided by 480 = 3333.33 amps has to be single phase amps.
1,600,00 divided by 480 and also divided again by 1.732 = 1924.56 would be the three phase amps.
If DC output is 1600 kVA @ 480 volts then it will be 3333.33 amps on the DC side but three phase AC side is only 1924.56 amps.
Funny it took till post 56 for someone to catch the amps calc math error !That would be single phase amps, if you deriving this from three phase then there is that 1.73 factor involved as mentioned and 1600kW three phase @ 480 volts would be 1924 amps, split across all three lines.
right. I’m rusty. I’ve spent the last 12 years developing low volt HVAC controls. But yes I forgot about the square root of 3. The Tesla data sheet did not list any amperage. Only 480vacFunny it took till post 56 for someone to catch the amps calc math error !![]()
Larry Fine first mentions it in post 50 a little more subtle but did mention it.Funny it took till post 56 for someone to catch the amps calc math error !![]()
I assuming this thing capable of charging multiple trucks at a time and has maximum rating of 1600 kW? If so unless you expect it to run at maximum rating for any amount of time I bet POCO doesn't supply you with 1600kVA transformer for it. Especially if they figure out it only sees 50% of that most of the time they likely only putting in maybe 750 kVA transformer. However from NEC perspective your supply conductors still needs be able to handle full rating as a general rule.We’re just trying to get this to make sense to the truck stop chain. They don’t see the grid connection usable to them, because of the demand charge costs. And who pays for the half-million $$ battery bank?
Another problem is what does the truck behind you do if you charge in front of them and you drain the battery from the charging station. ??
What then?
1,600 kW
50kW is individual truck charging capability?This is a 50kW level three charger powered by an 80hp micro turbine with a recouporator hx.
Charger is really sweet it’s data driven. It knows what EV you have when you connect.
But POCOs hate intermittent power use. It wrecks things for them.I assuming this thing capable of charging multiple trucks at a time and has maximum rating of 1600 kW? If so unless you expect it to run at maximum rating for any amount of time I bet POCO doesn't supply you with 1600kVA transformer for it. Especially if they figure out it only sees 50% of that most of the time they likely only putting in maybe 750 kVA transformer. However from NEC perspective your supply conductors still needs be able to handle full rating as a general rule.
There is lots of services out there that have undersized POCO transformers on them in comparison to the incoming service conductors. Typical dwellings are a good example as well. Lots of 200 amp services out there and only supplied by a 15 or 25 kVA transformer which are only 62.5 and 104 amp transformers. POCO's know they won't be loaded very high and if they are will be for short duration.
No that’s a car charger station.50kW is individual truck charging capability?