At 50kW
Fast charge DC
Fast charge DC
1600kw charging ability for 1 truck? does it come with a crane to handle the charging cable?The data sheet for the semi charger shows only 1 charge cable. It’s rated at 1600 kW by nameplate.
Yet they push on demand electric water heaters, but those aren't even close in kW to what we are talking about here either.But POCOs hate intermittent power use. It wrecks things for them.
You also need to realize that you can't use KW for calculating the supply equipment. You need to be using input KVA as that is what the supply equipment sees as I'm sure this will not be a unity PF load. Surely Tesla must specify the supply the ampacity of the supply side. In addition the code requires the supply equipment to be rated at 125% of the input amps.We’re just trying to get this to make sense to the truck stop chain. They don’t see the grid connection usable to them, because of the demand charge costs. And who pays for the half-million $$ battery bank?
Another problem is what does the truck behind you do if you charge in front of them and you drain the battery from the charging station. ??
What then?
right. I’m rusty. I’ve spent the last 12 years developing low volt HVAC controls. But yes I forgot about the square root of 3. The Tesla data sheet did not list any amperage. Only 480vac
1,600 kW
Yup. Our solution uses only 120vac 2 amp control power to keep the charger screens activated and can operate with the turbine off. Turbine supplies 50kW and up too 2000kW.So if this is powered by multiple sources, utility, on site generator, battery... seems best design would be having a common DC bus and each source only supplies whatever it it capable of to that bus and not necessarily total output capacity. If you want utility to be able to handle full 1600kW then it needs the large service mentioned. If you only want the utility to be able to provide say 50% of capacity then you could get by with smaller service and smaller rectifier. IMO multiple rectifiers would be a good idea. You could isolate a failed one and continue to use the other instead of total failure of this source.
The alternate sources also kind of presumes you are depending on different ones depending on conditions and/or cost of operating a particular source above a certain level -- like avoiding demand charges from POCO.
The battery I see as more of a "surge tank". Like having a large water tank that allows you to fill some other vessel rather quickly where the normal water supply can not deliver that kind of volume that quickly yet there is enough time between fills for it to recover before the next fill.
Not post #50?Funny it took till post 56 for someone to catch the amps calc math error !
Ah. Thank you. Granted, I didn't post the math.Larry Fine first mentions it in post 50 a little more subtle but did mention it.
For instance in one article the guy gets the average kWh number from Pacific Power at .13 cents, then divides the claimed kWh usage of the truck and is enthralled with this “extremely inexpensive” method for truck charging/traveling, unaware of the $20,000 per month demand charge that comes with it. Ratcheting / revolving demand charges are a huge barrier for the cyber truck and the semi truck.