The last big project where we installed them was a huge apartment complex. No one tested them when the building was constructed and I can assure you that no one will ever go back and test anything. And with good reason, testing would be a waste of time and money.I agree with infinity, they are installed per boiler plate spec. We used on traffic signal services to locate ground rods for ug work nearby
Cell tower sites have grounding out the wazoo. Lots of cadwelds.I can see somewhat of a case for them at a data center or cell tower. But a ufer ground is way better.
Where does it connect to? counterpoise?The last big project where we installed them was a huge apartment complex. No one tested them when the building was constructed and I can assure you that no one will ever go back and test anything. And with good reason, testing would be a waste of time and money.![]()
Yes, one of the 10' rods connected in a 3 rod triangle.Where does it connect to? counterpoise?
Then why can they not measure ground resistance at the ground rod where rod portion exposed above the ground?Yes, one of the 10' rods connected in a 3 rod triangle.
The test wells are in the floor of the basement. The rods are below the concrete floor.Then why can they not measure ground resistance at the ground rod where rod portion exposed above the ground?