I get 208.5A using 220.82 when I add a 32A EV charger. And now they have 40A and 48A and 80A chargers.I just did a load calc using 32 amps x4 for the water heater or 30,720 watts. I used 4,000 sq.ft added the typical range, dryer, microwave, dw, etc. I used 10000 watts for the a/c unit. I came up with 183 amps using the optional cal and 238 using the standard
That's not the optional calculation. See 220.82, for example.
What the City wants used for standardization. My guess.@ING23 . that is the standard calculation.
That is the method the City Use on their web site , I am not doing any job yet . This hole new community (all electric) has the same , more o less appliances. No idea how the builder get away with this. I just want to be sure I am not missing something here.@ING23 Did the city say you must use that calculation method? If so, then why did they pass the job
Well, it's quite possible as Dennis pointed out that with the optional load calc the installations comply with the NEC. (Stupid, in my opinion, but compliant.)That is the method the City Use on their web site , I am not doing any job yet . This hole new community (all electric) has the same , more o less appliances. No idea how the builder get away with this. I just want to be sure I am not missing something here.
This is because loads over i think either 40 or 50 amperes for dwellings have to be divided and a 150 ampere water heater on a 200 ampere service is hard or impossible to balance?My point was simply that a competent person doesn't install a 150A water heater on a 200A service for a single family home. You get a different water heater or a different size service.
Another way to put it is that most people don't bother to actually do load calcs for new single family homes, and just spec a 200A service. And most of the time that works out fine. But not with an electric on demand water heater.
I agree that the other details suggest that this wasn't the only aspect of the electrical that was rushed and sloppy.
Huh ?? a 240v load on a 240v service is pretty balanced !This is because loads over i think either 40 or 50 amperes for dwellings have to be divided and a 150 ampere water heater on a 200 ampere service is hard or impossible to balance?
If unbalanced loads such as this how does this affect things, voltages?
There is no such rule in the NEC I'm aware of. I've seen a steam shower on a 90A breaker, and car chargers on a 100A. It seems like for water heaters there may be something in the product standards because they all seem to be made this way after about 60A.This is because loads over i think either 40 or 50 amperes for dwellings have to be divided and a 150 ampere water heater on a 200 ampere service is hard or impossible to balance?
As augie said, this is not an unbalanced load on a single phase residential service. It might create some imbalance on the utility higher-voltage-level distribution network if there were a lot of these in one neighborhood and they weren't balanced, but that's above my pay grade. My guess is the utility might just need to replace/upgrade distribution transformers sooner than they wanted if they didn't get the heads up as the subdivision was going in.If unbalanced loads such as this how does this affect things, voltages?
there is such a code requiring (if i remember correctly) a specific appliance load over a certain amount to be divided within the power distribution panel but I do not have my code book as it’s at workThere is no such rule in the NEC I'm aware of. I've seen a steam shower on a 90A breaker, and car chargers on a 100A. It seems like for water heaters there may be something in the product standards because they all seem to be made this way after about 60A.
It would appear that this required by 422.11(B) in the 2020. It says in essence that a household appliance with surface heating elements with a demand greater than 60 amperes shall have the power supply subdivided into two or more circuits each with an OPCD not greater than 50 amperes.there is such a code requiring (if i remember correctly) a specific appliance load over a certain amount to be divided within the power distribution panel but I do not have my code book as it’s at work