Joseph1970
- Ohio
- Electrician
I have a square d 480 volt starter with 480 volt coil how do I wire this up with a start stop button
Did you make it?
No, just found it with a quick Google image search, like I do most images I post.Did you make it?
Might not be required, but I'd like to see fuses on the control wiring.
A couple class CC fuses do save a lot of damage when the coil reaches EOL.Might not be required, but I'd like to see fuses on the control wiring.
Table 430.72(B)(2) shows the requires protection for control circuits tapped off of the motor power circuit, but permits a motor power circuit with a branch circuit OCPD of 45 amps to protect a 14 AWG control circuit.Might not be required, but I'd like to see fuses on the control wiring.
Stand alone Pump Panels come standard with line voltage controls. Fusing will vary with supplier.Assuming this is a real device and not a test question: Make sure you buy 600 V pushbuttons. While 480 V control is perfectly legal per the NEC, I'd strongly advise replacing the 480 V coil with a 120 V coil and installing a control power transformer. Running 480 V pushbuttons and switches is an idea whose time has passed.
Depends on contactor/coil design.A couple class CC fuses do save a lot of damage when the coil reaches EOL.
Too many times I've seen it take PB and/or overload contacts along with it.Depends on contactor/coil design.
Two most common types of pump panels I run into on irrigation are Square D and Siemens. Square D coils are usually easy to replace. Siemens almost always swell up and you have a hard time taking it apart to replace the coil. Even if the Square D does swell up, it is just designed differently and easier to gain access to deal with the issue.
It doesn't. We diverged a bit with discussion of control fusing but don't think PPs are only used for pumps in the real world.I didn't see where the OP said this was for a pump motor.
Did you mean combination starters?I think NEMA MCCs still have line voltage control as the minimum standard. It doesn't mean you can't spec something better and safer.
I believe you can order the MCC with line voltage control circuits if you want to....have not seen that in decades.Did you mean combination starters?
Don't most MCCs have a control transformer in every bucket usually either 120 or 24 VAC for control voltage?
I can't imagine there being much demand for 480 volt control circuits with an MCC.I believe you can order the MCC with line voltage control circuits if you want to....have not seen that in decades.
There is not.I can't imagine there being much demand for 480 volt control circuits with an MCC.
The larger the MCC the less it might be desired, unless maybe every single motor were very related to one another in a particular process/sub process of the facility.
I can see 120 volt contactor coils being more desirable to be installed if the MCC were supplied by 208/120 and each supplied by line voltage rather than via control transformers though.
You still talking about MCC's I assume.There is not.
The only time I have seen it in the past 20 years or so, was only for the coil on size 4 and 5 starters, but even there there was an interposing relay and 120 volt CPT and control circuit. The coils for larger starters will require a much larger CPT if the coil voltage is 120 and the use of a 480 volt coil solves that issue.
The last time I saw an actual 480 volt control circuit was in the 70s at an old industrial plant.