• Three-phase: four-wire 240/120 open delta* volts nominal.
*The service size for this three-phase four-wire 240/120 volt open delta connection shall be
limited to a total of 200 amps per transformer bank. An open delta connection can create
current and voltage unbalances that could potentially damage the Customer’s equipment.
Certain types of equipment, such as motors and refrigeration compressors, are more suscep-
tible to damage with this type of connection. Upgrades of existing delta connections beyond
200 amps are classified as a non-standard voltage connection.
ITs interesting, Seattle city light says the same thing where they only list "open delta" specifically, with apparently no option for a closed delta![]()
We don't do new 'open' delta unless we have to avoid a primary extension.
And I think that is the source of the confusion 'full' delta is still done.
The ABB 'MTP Mini' line is a excellent all in one three phase padmounted transformer that offers self contained units for:
208Y/120, 216Y/125, 460Y/265, 480Y/277, 480∆,
240∆ and 240∆ with 120 volt mid-tap in one phase