Hi Moderator,
I stumbled into the gray area when I was trying to figure out a design issue on how to incorporate an existing manual transfer switch for a generator into a new 600amp 480volt 3phase 4wire Y electrical service. Customer currently has 400amp 240/120volt 1phase 3 wire service, 2hots, 1neutral. I would be upgrading that to the 3phase service. I spoke to POCO about the new service having unbalanced loads coupled with the fact I would have to rewire the building and was reasonably told "it is what it is". Will wait and see what happens when I fill out work request. The new service rated MDP has a 600 amp MCB and 30 branch breakers. So I don't have to rewire the building I plan on refeeding the existing 400 amp 1phase "service" panel with 2poles of a 3pole breaker from MDP through a new 100kVA 480Volt to 240volt 1phase transformer via the existing manual transfer switch. The existing 400amp panel's MCB would be more than 10' from secondary side of new transformer. To comply with NEC 2023 I plan on installing a 400amp 2 pole fused disco.
So here's the gray area question… in black bold…regarding turns ratio and calculations.
Is there a mistake in NEC 2023 Hardcover Article 240.21(C)(2)(4) Calculation Example on Page 198?
Turns ratio in NEC Article says 480/208. Mike Holt Forum Article posted 10/2/2010 reply#4 says turns ratio is 480/120.
Question: Who is correct? If both, what don’t I understand?
10/2/2010 Forum is written as follows:
Overcurrent Protection for Transformers and Automatic Transfer Switches
Got into a pretty heated argument recently with a colleague and hoping that you guys can help clear this up.
First, a 480 - 208/120V delta-wye transformer is being installed and is being fed on the primary side from a switchboard breaker. On the secondary side, is another breaker necessary? I said yes and in the NEC Article 240.4(F) it says it pretty explicitly
"Single-phase and multiphase transformer secondary conductors shall not be considered to be protected by the primary overcurrent protective device"
There are a couple of exceptions given (a single-phase 2 wire or a delta-delta 3 phase transformer can be considered protected on the secondary side just by having a primary breaker) but it seems pretty clear that secondary breaker is needed.
The second question is for an Automatic Transfer Switches, if I have a breaker protecting the Normal feeder and the Emergency feeder, do I need a breaker to protect the Load feeder. My colleague says no. I think yes, but I am not as sure about this one. Couldn't find anything in the code about this.
Massachusetts
#2
I agree with you, the transformer may not require secondary protection but the conductors do require protection.
Here I disagree with you. Assuming that the 'load feeders' rating is equal to or exceeds the rating of the normal and emergency feeder breakers you do not need to add another breaker.
#3
Thanks iwire.
What is the technical explanation though?
In the NEC handbook it delves deeper into this and says that a single phase 120V overload could cause sufficient current to cause problems for the secondary conductors but not trip the breaker on the primary (480V) side. However, I don't understand how that could happen.
In a balanced or unbalanced wye system, the phase (Ian) currents are the same as their respective line currents (Ia). So, lets say I had a 75KVA (480 - 208/120V) transformer. I would have a 100A breaker on the primary side. On the secondary side, my conductors would be rated to handle 250A. If I had an overload on one of my single phase loads and it started drawing 300A. The primary side, 100A breaker would see 300 * (208/480) = 130A on one of the phases and would trip.
That is what my colleague is thinking and I can't really disprove this. Any thoughts?
Esteemed Member
Ohio
#4
... The primary side, 100A breaker would see 300 * (208/480) = 130A on one of the phases and would trip.
The voltage ratio is 120/480, i.e. secondary to primary winding. Two primary lines, with no other loads, would only see 75A.
New York City
#5
Asuming we are talking about the transfer switch, the load side will always be protracted for the breaker on the normal feeders or if the transfer switch is actived the EM load side breakers will protect your load side wire on the TS
Now I assume that the wire size of your load side of the transfer switch is the same size as your normal power and your EM power wire size!!!
- Thread starterMachiavelli999
- Start dateOct 2, 2010
Massachusetts
#2
#3
Thanks iwire.
Esteemed Member
Ohio
#4
New York City
#5