Jody Boehs
- Fairview, Oklahoma, USA
- Controls and Electrical Manager
Then that transformer is just what you need.I have 480 wye with no neutral. I need 240 3 phase.
Then you need not ask about a primary neutral.I have 480 wye with no neutral.
Absolutely, and having the wye secondary would make grounding it simple.I need 240 3 phase.
would 240 wye work? i know i wont be able to use any single phase off of it but would it work
Agreed, except for:Then that transformer is just what you need.
. . . you would have to ground the center tap, corner-ground, or use fault-detection.
so which one the first one i posted or the wye to wyeThen that transformer is just what you need.
i hope those are readily availableThen you need not ask about a primary neutral.
Otherwise, you would have to ground the center tap, corner-ground, or use fault-detection.
He's referring to the delta-delta you posted. It suits your source and required voltages.so which one the first one i posted or the wye to wye
Yes a secondary of 208Y/120 is very common, but if he needs 240 volts line to line, a secondary of 240Y/139 is less common.He's referring to the delta-delta you posted. It suits your source and required voltages.
But it doesn't make for symmetrical grounding. Ideally, you want a delta-to-wye transformer.
And, yes, they are relatively common.
They aren't that hard to find, and VFD use has made them more popular.Yes a secondary of 208Y/120 is very common, but if he needs 240 volts line to line, a secondary of 240Y/139 is less common.
You neither need nor want a wye primary.can I use a delta to wye transformer on my 480 wye primary? i think i have before
Yes, it will work, and if you might have use for the 120v or 120/240v, then definitely.If i can use the first transformer i posted then thats what I will do. the symmetrical grounding im not too familiar with
awesome thank youYes, it will work, and if you might have use for the 120v or 120/240v, then definitely.
By symmetrical, I meant equal line-to-neutral voltages, like a wye normally has.
Yes.You're welcome.
To recap:
The primary will be the three lines plus an EGC; no neutral.
The secondary will be three lines (one hi-leg) and a neutral.